I use CH almost everywhere. I bought 100 amp main breaker panel for a rural shop building. I frequently use a ML panel and back feed a 100 or 70 or 90 CB but the 100MB with plug on neutral was less expensive. Nice until you go to put a 2 pole GFCI in for Air Compressor receptacle. They don't fit and CH doesn't make a plug on style. Huh??:jawdrop:.

The only solution is to set a small sub next to the brand new panel. :thumbsdown:
 

eds

Senior Member
I also use CH and the plug on neutral panels are the only style my supply house carries, are you saying all GFI breakers wont fit?
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Tried some CH-CH loadcenters a few years ago for one of our farm customers new offices. The breakers kept popping off the buss.

Tried a CH CH metermain for an overhead service. Couldn't flip the line side lugs for a top feed like Siemens, had to chase overhead wires down behind the jaws and curl back up into the lugs. Was a total pain in the ###.

No more CH for me.
 