All the 5kw shop heaters I'm used to dealing with (Marley/Qmark) have the temperature adjustment on the unit itself. That control allows the fan to run after the unit "thermostat" is satisfied.
The 10kw size I've installed have a contactor that can be controlled by a low voltage t-stat mounted on the wall. The contactor shuts off the heating element but allows the fan to run afterwards until the elements cool down.
Is there an option to set up a 5kw with a remote t-stat (wall-mount) that allows the fan to run afterwards without majorly rewiring the the heater? Maybe install a 2-pole contactor internal to the heater that only cuts out power to the heat elements, allowing the fan to continue to run?
I'm working on a building that has 14-foot sidewalls. It's mostly for storage, but they want a 5kw to keep it in the 45-55 range. Getting up on a ladder to adjust the dial isn't an option.
Thanks
The 10kw size I've installed have a contactor that can be controlled by a low voltage t-stat mounted on the wall. The contactor shuts off the heating element but allows the fan to run afterwards until the elements cool down.
Is there an option to set up a 5kw with a remote t-stat (wall-mount) that allows the fan to run afterwards without majorly rewiring the the heater? Maybe install a 2-pole contactor internal to the heater that only cuts out power to the heat elements, allowing the fan to continue to run?
I'm working on a building that has 14-foot sidewalls. It's mostly for storage, but they want a 5kw to keep it in the 45-55 range. Getting up on a ladder to adjust the dial isn't an option.
Thanks