Electrical Heat Trace - Different rate wattage on same circuit

Status
Not open for further replies.

MrJLH

Senior Member
Location
CO
Came across this yesterday on electrical heat trace:

Can for example 8W/ft electrical heat trace say 30 feet, be wired through conductors and conduit to say 5W/ft electrical heat trace on the same circuit?
Thanks
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
As long as they're designed for the same voltage, sure. Same as putting an 8-watt lightbulb on the same circuit as a 5-watt lightbulb.
But I'm compelled to ask, "Why?". Why are two different power densities installed in the same environment? Seems like the thermal engineering needs to be reviewed.
 

MrJLH

Senior Member
Location
CO
As long as they're designed for the same voltage, sure. Same as putting an 8-watt lightbulb on the same circuit as a 5-watt lightbulb.
But I'm compelled to ask, "Why?". Why are two different power densities installed in the same environment? Seems like the thermal engineering needs to be reviewed.

What happened a drain line for a hydrocarbon condenser was designed using 8W/ft, and the actual condenser came pre-traced from the vendor with 5W/ft. Seems logical in my head, but wanted some thoughts.

Thanks
 