I was wondering if there is an alternative to duct seal when filling holes with cables, 600MCM in a 4” pvc conduit. Maybe a fire stop spray foam. Will it deteriorate the insulation on a THHN, XHHW
 

tom baker

First Chief Moderator
Staff member
Any product for use in sealing cables, needs to be identified for the use, spray foam is not, the polywater is. See 300.5 (G) I have used the polywater, good clear instructions and it can be removed later, which I have done
 