I have a service disconnect that is about 100 ft away from the load center it's feeding. There is a driven rod at that location. The conductors are in rigid metal conduit from the disconnect to the load center. 2 insulated ungrounded conductors and a bare grounded conductor-make up the feed, conduit is used as EG.
A copper water line is present inside the building where the load center is. Is it code compliant to connect the water line to the load center EG bar that is isolated from the grounded conductor in the load center?
Ground bushings and jumpers will be used at both ends of the rigid metal conduit.
I've never run into this scenario before.
Thanks .