    Fire Alarm Bell and Signal Light

    Is this still permitted in new buildings?


    https://www.flickr.com/photos/138908...n/photostream/

    #2
    Originally posted by mbrooke View Post
    Is this still permitted in new buildings?


    https://www.flickr.com/photos/138908...n/photostream/
    I found a lot of these types of installations in NYC when I worked there. Years ago, when Acme was the big FA manufacturer they came up with a lot of these "made in your garage" type pieces of equipment. We've come a long way since then.

    Comment


      #3
      Originally posted by mbrooke View Post
      Is this still permitted in new buildings?


      https://www.flickr.com/photos/138908...n/photostream/
      If it's considered auxiliary signaling or notification and it can't negatively affect the panel operation, it would be permitted IMO. The AHJ's reaction may be to red-flag it, but unless he/she can make the case that it would impair the operation of the panel or occupant notification, you could make a good case that it can stay. Something like that, on the other hand, is likely being required by the AHJ.

      Comment


        #4
        Originally posted by gadfly56 View Post

        If it's considered auxiliary signaling or notification and it can't negatively affect the panel operation, it would be permitted IMO. The AHJ's reaction may be to red-flag it, but unless he/she can make the case that it would impair the operation of the panel or occupant notification, you could make a good case that it can stay. Something like that, on the other hand, is likely being required by the AHJ.
        Auxiliary- but can't be main- correct?

        Comment


          #5
          Originally posted by gadfly56 View Post

          If it's considered auxiliary signaling or notification and it can't negatively affect the panel operation, it would be permitted IMO. The AHJ's reaction may be to red-flag it, but unless he/she can make the case that it would impair the operation of the panel or occupant notification, you could make a good case that it can stay. Something like that, on the other hand, is likely being required by the AHJ.
          AND, from what I remember it has to be approved by the Board of Standards and Appeals.