goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I'm doing some work at an ambulance corps building in my home town. They would like to have the garage lights come on when they are backing the rigs into the garage. They currently have 3 bays where there are a set of three two-lamp 8' T-8 fluorescent lights on either side of each rig. I've already converted one set (6 lamps) to LED's wired direct. The lighting circuit is currently drawing 10+ amps. There are also two 3-ways and two 4-ways in the switching scenario. I was thinking about using a Caseta Pro switch, leaving one 3-way and both 4-ways in place and providing each rig with a visor clip remote. However, the Caseta switch is only rated for 5 amps. Does anyone have any suggestions for another method of switching in this scenario?
Thanks in advance.
Thanks in advance.