    Shielded 600V Feeder Cable

    Does anyone have any information on why it would be advantageous to install shielded feeder cable to the incoming AC section on a VFD lineup vs non-shielded? Or if braided straps would stop harmonics from polluting up the line. I can understand using it for the load side of the VFD but do not understand, fully, for the line side prior the filter, which already contains an isolation transformer.
    I just can't fathom the reasoning behind it, especially since 3c/750 w/g shld is around 80 dollars a foot. Then again I am not an engineer.
    Thanks in advance.

    #2
    Originally posted by Breaker19 View Post
    Does anyone have any information on why it would be advantageous to install shielded feeder cable to the incoming AC section on a VFD lineup vs non-shielded? Or if braided straps would stop harmonics from polluting up the line. I can understand using it for the load side of the VFD but do not understand, fully, for the line side prior the filter, which already contains an isolation transformer.
    I just can't fathom the reasoning behind it, especially since 3c/750 w/g shld is around 80 dollars a foot. Then again I am not an engineer.
    Thanks in advance.
    Running the cables in grounded EMC already provides excellent shielding.

    Comment


      #3
      The idea behind shielding is to prevent the cables from becoming radio transmitting antennae. If you are laying them in tray, shielding is a must. If pulling them in grounded conduit, as Electric-Light said the conduit serves the same function. Pulling shielded cable inside of grounded conduit is a waste IMHO.
      __________________________________________________ ____________________________
      Many people are shocked when they discover I am not a good electrician...

      I'm in California, ergo I am still stuck on the 2014 NEC... We'll get around to the 2017 code in around 2021.

      Comment


        #4
        Jraef is correct. Two engineers from Belden and one from Rockwell wrote a paper about this that was presented at the 1999 IEEE PCIC conference. It's one of the best papers out there on VFD cabling - this feeder cable antenna effect is just one of a number of topics covered. They also discuss the life expectancy of various cable insulations under years of reflected wave voltage pulses - this is the only place I've seen any serious analysis on VFD cable life.