Class I equipment in Class II locations

Status
Not open for further replies.

HazInspector

Member
Location
NZ
I was wondering if someone could point me in the direction of any clause that would allow (or not allow) this?
We have a device approved for Class 1 Div 1 locations but the client wants to install in Class 2 Div 2 location.

Any assistance would be appreciated.
 

bphgravity

Senior Member
Location
Florida
2014 NEC:

502.5 Explosionproof Equipment

"Explosionproof equipment and wiring shall not be required and
shall not be acceptable in Class II locations unless also identified
for such locations."
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
2014 NEC:

502.5 Explosionproof Equipment

"Explosionproof equipment and wiring shall not be required and
shall not be acceptable in Class II locations unless also identified
for such locations."

while this is true, the requirements for CIID2 are pretty relaxed and it may well be that your explosion proof equipment also meets the requirements for being in such an area. IIRC, enclosures are generally only required to be dust tight.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In general, most non-heat producing devices that are marked for use in Class I locations, are also marked for use in Class II locations.
 