class1 division1 camera hook ups

Status
Not open for further replies.

pappasmurf

New member
so im running pipe for cameras that are explosion proof encased in a class1 division 1 building ,my question is their a flex able pipe I can use to connect to the cameras or do I have to run rigid directly into the cameras and if so do I have to use seals at those connections
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
so im running pipe for cameras that are explosion proof encased in a class1 division 1 building ,my question is their a flex able pipe I can use to connect to the cameras or do I have to run rigid directly into the cameras and if so do I have to use seals at those connections
They are called explosionproof flexible couplings. You will still have to seal the enclosure.
 