I have a type Z purged enclosure. Can I mount a standard rotary disconnect inside of this enclosure, given that I can maintain the positive pressure after mounting the rotary handle on the enclosre door? I have mostly worked with Type X purged enclosures that require that the all the electronics inside of the enclosure to shut down if the door to the enclosure is opened. Type Z purge does not have that requirement.
I would think that it would be best to have the disconnect inside of an explosion proof enclosure because in the worst possible scenario you would want to be able to disconnect the machine from the supply.
I do not see anything in NFPA 496 that says you have to have the disconnect in an explosion proof enclosure. Is this only a requirement for Type X purge?
I would think that it would be best to have the disconnect inside of an explosion proof enclosure because in the worst possible scenario you would want to be able to disconnect the machine from the supply.
I do not see anything in NFPA 496 that says you have to have the disconnect in an explosion proof enclosure. Is this only a requirement for Type X purge?