NEMA for VFD

Status
Not open for further replies.
i am designing a new system for circulation Toluene. my question is i have the VFD for the motor, and the VFD need to be in NEMA box , do i need to have Z-purge system to complies with NEC code ?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
No purging process is allowed in the motor enclosure. Nema enclosures must isolate the electrical equipment from other environments. Higher NEMA ratings are required for more severe environments.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Both NEMA MG-1 and the NEC permit purging motor enclosures. See Section 501.125(A)(2) for a Class I, Division1 example. Section 501.125(B)(2) refers back to Division 1 for some Division 2 applications, if appropriate. Usually Division 1 identified motors are not required in Division 2; however, NEMA MG-1 does require the motor manufacturer’s input where their motor is used with a ASD (VFD) in a classified location.

However, I believe the OP was asking about the ASD (VFD) enclosure. It too may use a Type Z purge, assuming it is a Division 2 application.
 