    cable in conduit cable end seals

    what do you all use for end sealing cables, crouse hinds epoxy TSC? it isn't clearly labelled for this. what else is available?

    i'm talking about when you run cable capable of transmitting gases in rigid, don't open the jacket in the seal off but seal the cable end in the enclosure where it terminates.

    #2
    Are we talking about multiconductor cable in conduit?
    [COLOR=black]"Bob"[/COLOR]
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.

    Comment


      #3
      Originally posted by Wire-Smith View Post
      what do you all use for end sealing cables, crouse hinds epoxy TSC? it isn't clearly labelled for this. what else is available?

      i'm talking about when you run cable capable of transmitting gases in rigid, don't open the jacket in the seal off but seal the cable end in the enclosure where it terminates.

      If you were running ONLY multiconductor cable such as TC-ER or MC-HL (no conduit) you could use the TSC Epoxy Sealing compound along with a TMCX connector. But since the cable is routed within conduit, I believe you'll to have to use a conduit seal - such as EYS - open the jacket/separate the conductors and apply Chico compound.

      Comment


        #4
        Originally posted by rbalex View Post
        Are we talking about multiconductor cable in conduit?
        yes

        Comment


          #5
          Originally posted by Dale001289 View Post
          If you were running ONLY multiconductor cable such as TC-ER or MC-HL (no conduit) you could use the TSC Epoxy Sealing compound along with a TMCX connector. But since the cable is routed within conduit, I believe you'll to have to use a conduit seal - such as EYS - open the jacket/separate the conductors and apply Chico compound.
          i disagree 501.15(D)(2) exception

          cable w/ gas/vapor-tight sheath

          Comment


            #6
            Originally posted by Wire-Smith View Post
            i disagree 501.15(D)(2) exception

            cable w/ gas/vapor-tight sheath
            The cable sheath is not the cable core - That’s why you need the EYS/Chico etc


            Sent from my iPhone using Tapatalk

            Comment


              #7
              Originally posted by Dale001289 View Post
              The cable sheath is not the cable core - That’s why you need the EYS/Chico etc


              Sent from my iPhone using Tapatalk

              did u read the exception, you don't have to open the sheath in a seal-off, just seal cable end at termination

              Comment


                #8
                Originally posted by Wire-Smith View Post
                did u read the exception, you don't have to open the sheath in a seal-off, just seal cable end at termination
                There is no approved UL sealant for multiconductor cable ends when installed in conduit - you need a tmcx for that


                Sent from my iPhone using Tapatalk

                Comment


                  #9
                  Originally posted by Dale001289 View Post
                  There is no approved UL sealant for multiconductor cable ends when installed in conduit - you need a tmcx for that


                  Sent from my iPhone using Tapatalk
                  doesnt need to be ul approved, just approved (by ahj)

                  Comment


                    #10
                    Originally posted by Wire-Smith View Post
                    doesnt need to be ul approved, just approved (by ahj)
                    Wrong.


                    Sent from my iPhone using Tapatalk

                    Comment


                      #11
                      Originally posted by Dale001289 View Post
                      Wrong.


                      Sent from my iPhone using Tapatalk
                      code reference please

                      Comment


                        #12
                        Originally posted by Dale001289 View Post
                        Wrong.
                        [QUOTE=Dale001289;1919231]


                        501.15(D)(2) exception

                        ....by an approved means.....


                        article 100

                        Approved- acceptable to the authority having jurisdiction

                        Comment


                          #13
                          Originally posted by Wire-Smith View Post
                          501.15(D)(2) exception

                          ....by an approved means.....


                          article 100

                          Approved- acceptable to the authority having jurisdiction
                          “Approved“ and “Approved Means” are not the same thing -


                          Sent from my iPhone using Tapatalk

                          Comment


                            #14
                            Originally posted by Dale001289 View Post
                            Wrong.
                            are you thinking of listed? its different

                            Comment


                              #15
                              Originally posted by Dale001289 View Post
                              “Approved“ and “Approved Means” are not the same thing -


                              Sent from my iPhone using Tapatalk
                              110.2 Approval. "the conductors and equipment required or permitted by this code shall be acceptable only if approved.

                              informational note. see... definitions of approved....."


                              once again, code reference please. i don't subscribe to dales electrical code just NEC


                              means
                              mēnz/
                              noun
                              [COLOR=#878787 !important][/COLOR]
                              [LIST][*]1.
                              an action or system by which a result is brought about; a method.[/LIST]
                              put the two together and what do you have?

                              Comment