Conduit entering in Manhole

Status
Not open for further replies.

smarteng

Member
Location
Los Angeles
Hello Sir/Madam,

I have a conduit coming out of an equipment. Equipment is in Class 1 Area 1. Conduit is sealed at equipment end. Same conduit later enter in a Manhole ( about 20'). Do I need to take any precaution with manhole, like seal in Manhole or explosion proof Manhole. Manhole is out of Classification area. Please advise.

Thank you.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Hello Sir/Madam,

I have a conduit coming out of an equipment. Equipment is in Class 1 Area 1. Conduit is sealed at equipment end. Same conduit later enter in a Manhole ( about 20'). Do I need to take any precaution with manhole, like seal in Manhole or explosion proof Manhole. Manhole is out of Classification area. Please advise.

Thank you.
First, we are going to assume you mean Class I, Division 1. If that is not true you need to clear it up.

Second, we are going to assume that no Article from 511 to 515 applies. Again, if that assumption is not correct you need to clear it up.

Third, we will assume the seals in the Class I, Division 1 location and at the boundary, if the equipment seal don’t do double duty, are properly installed.

Fourth, we assume you are certain there is no Division 2 that encloses the Division 1 location and it extends above the manhole. At 20’ from the Division 1, location a Division 2 location above the manhole would be expected.

If the assumptions are correct, nothing special needs to be done in the manhole.
 

smarteng

Member
Location
Los Angeles
Thank you so much for the reply.

1. My Bad, it is class I Div 1.
2.
3. Yes All Class 1 Div 1 equipment conduits are Sealed
4. No Class 1 Div 2 exist over Manhole.

Regards.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Thank you so much for the reply.

1. My Bad, it is class I Div 1.
2.
3. Yes All Class 1 Div 1 equipment conduits are Sealed
4. No Class 1 Div 2 exist over Manhole.

Regards.
1 The "C" in "Class" is capitalized.
3&4 For hazardous locations "Class" is designated with Roman numerals: I, II, III

No big, but if you are going to be a smart engineer, you should know.;)
 