Pouring conduit seal offs

Status
Not open for further replies.

Red gypsy

Member
Location
delaware
Recently at work a coworker and i have had a discrepancy about how to pour sealoffs. He believes that a Crouse Hinds eysx seal off (http://www.cooperindustries.com/con...fillexplosionproofconduitsealingfittings.html) used in a vertical application only has to be filled 1/3rd the way up the seal off so when you remove the plug you can visually inspect it to see that the wires have been separated. I however pour until i can visually see the sealing compound reach the small plug. I have looked online for manufactures instructions on how to properly pour them and i have not found much in regards to the proper amount to put in the seal off. If anyone with a little more knowledge on the subject could help us out it would greatly be appreciated.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Checking with the manufacturer's instructions is a good ideal; however, see Section 501.15(C)(3).
 

Red gypsy

Member
Location
delaware
Thank you for your response, I read section 501.15 (c)(3) and from what i have gathered it requires that it shall not be less then the trade size used. In our case it was inch and a half so i believe from the fiber dam to the top of the sealing compound it should measure the trade size we used of 1 1/2". And in no case should it ever be below 5/8 of an inch. Again thank you for your response.
 