Re: Induction Motors Classified area
You?ve changed the question.
You asked "...can we use TEFC induction motors with Class B insulation", not the rationale behind it.
Go back to 430.7(A)(5). It?s one of the required [NEMA] markings on motors. It may either be the, ?Rated temperature rise or the insulation system class and rated ambient temperature.? Also note I originally used the term
Class B rise rather than
Class B insulation; they aren?t necessarily the same thing although a
Class B insulation implies no greater than a
Class B rise.
Per NEMA MG-1, a Class B rise implies not more than an 80 to 90C temperature rise over a 40C ambient depending on temperature measurement means and application and construction of the motor. In any case, the maximum temperature is 130C, well within the limits of the AIT you specified.
Because this is Division 2, the emphasis is on ?normal operation? use of the motor. See the end of the sentence in 502.8(B). Also see 500.8(A)(5).
If you are saying you prefer to use a motor identified for Class II, Division 1 go ahead.