nhee is correct that there are no enclosures rated specifically for Division 2, although there are some types of hazardous location equipment, such as some lighting fixtures, that may only have a Division 2 rating.
As a general rule in Division 2, cables listed in [2002] 501.4(B)(4) through (6) as wiring methods may be installed per their appropriate Chapter 3 Article or Articles 725 or 727 as applicable. The only additional requirements, as wiring methods, are detailed in the referenced subsections [501.4(B)(4) through (6)] and usually calls for additional attention to tensile stress. This does NOT necessarily require special termination fittings beyond what would already be required in ordinary locations for abrasion; only that tensile stress (pull-out) is given special attention.
The significant termination requirements, as cables, are described in [2002] 501.5(E)(1). Unless the enclosure is required to be explosion proof there are no additional requirements beyond those listed in 501.4(B)(4) through (6). If the enclosure is required to be explosion proof, Section 501.5(E)(1) describes the methods necessary to maintain the integrity of the enclosure.