The installation of Sealtite (liquidtight flexible metal conduit) in a class I, Div 2 area is permitted "...where provision must be made for limited flexibility." [Article 501.4(B)(2)] What is meant by the word "must" in this context?
I often see installations where 3-feet sections of Sealtite, with external bonding jumpers, are used to connect process instruments to RMC conduit systems. Replacement instruments often have different physical dimensions than original equipment and using Sealtite GREATLY facilitates this exchange. Is this permitted? (Assuming the instrument has seals properly installed.)
Corollary: If a full-size equipment ground is installed inside the Sealtite, can a Sealtite connector (non-tapered threads) be attached directly to a threaded conduit coupling? Or does the Sealtite need to connect to a fitting which has tapered threads?
I often see installations where 3-feet sections of Sealtite, with external bonding jumpers, are used to connect process instruments to RMC conduit systems. Replacement instruments often have different physical dimensions than original equipment and using Sealtite GREATLY facilitates this exchange. Is this permitted? (Assuming the instrument has seals properly installed.)