Announcement
Collapse
No announcement yet.
Waste oil desposal tank inside of a shipping container
Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts
    Does anyone know if a Waste Oil recycle storage tank and Oil Filter Crusher , located inside of a Shipping Container , where a person walks in and dumps used oil into a tank would be considered a Classified Location ? Studied NFPA , NEC understand gasoline and other flammables , can't find Oil , other than it has a higher flash point as a combustible not sure about its classification or wiring methods . Help would be greatly appreciated . Thanks !
    #2
    It does not give off easily ignitable gases under normal temp and pressure conditions like gasoline does, those gases are what causes the classification.
    I live for today, I'm just a day behind.
    Comment
      #3
      Thanks , getting mixed info on NFPA classification weather its 111b flash point 200 F or above same as cooking oil , or class 11 101 F - 140 F same as diesel . Do you happen to know which one ?
      Comment
        #4
        In your particular case it doesn't matter whether it is Class II or Class IIIB. See NFPA 497, Section 4.2.7. If you still have a concern, consult with a relevant MSDS.
        "Bob"
        Robert B. Alexander, P.E.
        Answers based on 2017 NEC unless otherwise noted.
        Comment
        Working...
        X