are there any lbs suitable for class2 div2 what company could supply them ? could sealing putty be used instead on a regular lb as a other method
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Any listed LB that meets the requirements of Section 502.10(B)(4) is suitable for Class II, Division 2. Virtually any manufacturer of listed LBs makes them.

Sealing is in Class II is actually simple. See Section 502.15. (It applies to both Division 1 and 2)
 