classification of generator building

Status
Not open for further replies.

gmayeux

Member
when installing electrical devices(lighting, electrical panels etc..) in an enclosure or small building housing 2- 125kva diesel generators, does the electrical equipment need to be designed for classifed area. the generators will have day tanks built on to them.
 

rcwilson

Senior Member
Location
Redmond, WA
Diesel generator areas are seldom classified. Doesn't make sense to classify all the elelctrical equipment to prevent ignition from arcing or high temperature when the engine components are just as hot.

Also, diesel fuel is usually not classifed. It is usually not an explosive mixture like propane, gasoline or natural gas.

If the engines run on propane or natural gas, there may be a need to classify.
 

bobgorno

Senior Member
Location
Colorado
NFPA 37 (2010) Installation and Use of Stationary Combustion Engines and Gas Turbines, Chapter 4.5.2
Fuel, lube oil, don't require you to classify.
 