EGC terminated on neutral buss

Status
Not open for further replies.

Danpc1979

Member
Location
Cranston RI
I always terminate my egc on the ground buss in a main panel that has a bonded neutral and ground buss. The guestion is: can the egc terminate on the bonded neutral buss ?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If the panel contains the main or system bonding jumper, you can connect the EGC to the neural bus.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I always terminate my egc on the ground buss in a main panel that has a bonded neutral and ground buss. The guestion is: can the egc terminate on the bonded neutral buss ?

Yes, but I, like you keep them separate. The neutral however may not be allowed to terminate on the ground bar if the only connection is thru the can.
 