I had a building that was changed from a C1D2 location to a C1D1 location. The building currently has liquid tight mettalic flex running to some motors and other equipment. What kind of flexible conduit is available to run to this equipment now that it is a C1D1 location?
Thanks
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
See Section 501.10(A)(2). Technically, there are no "flexible conduits." However, there are flexible fittings - they are exceptionally expensive.

This Section also refers to Section 501.140 for applications of "Flexible Cords." The approved applications are very limited though.
 

james_mcquade

Senior Member
We use explosion proof felxible conduit at some of the plants i work in.
i believe that crouse-hinds is the manufacturer. I will try tomorrow to get the manufacturer info.

regards,
james
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
We use explosion proof felxible conduit at some of the plants i work in.
i believe that crouse-hinds is the manufacturer. I will try tomorrow to get the manufacturer info.

regards,
james
The link in post #2 is to the Crouse Hinds product, but the point is that it is not called "flexible conduit" by the manufacturer.
 

james_mcquade

Senior Member
Sorry it took so long in getting back to you.

Crouse Hinds.
i have some part numbers as a feference.
ECLK115 AND ECGJH118

Explosion Proof Conduit Flexible Coupling is what i found on several websites.

regards,
James
 