Class 1 Div I Seals

Status
Not open for further replies.

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
No, but why do you have "Class 1, Div I seal" as the title of your post? What is the realtionship between the two? ...
I suspect it was raised by reviewing 501.15(A)(1)(2) or possibly by an influence from the IEC world where terminals are considered to be arc-making.
 

markstg

Senior Member
Location
Big Easy
I would think that in Class 1 Div 1 locations abnormal circuit conditions must be considered, so terminal boxes need to be Explosion Proof to account for faulted wire conditions. Whereas in Class 1 Div 2 normal circuit operations are all that is required to be considered so terminal boxes are not required to be Explosion Proof since no faults under normal circuit operation.
 