petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
Say you are an inspector.
Would you accept a control panel for use in a Class I division 2 area under one or more of the following conditions.
- not a listed panel
- a UL listed control panel under UL508a but that used all internal components UL listed as suitable for use in a C1D2 area
- a non UL listed panel with a UL listed purge system suitable for C1D2
- a UL listed panel with a UL listed purge system
- not a UL listed panel but all internal components are listed for use in a C1D2 area OR have no make/break contacts and are in a GP enclosure as per 501.105(B) (3)
why?
Would you accept a control panel for use in a Class I division 2 area under one or more of the following conditions.
- not a listed panel
- a UL listed control panel under UL508a but that used all internal components UL listed as suitable for use in a C1D2 area
- a non UL listed panel with a UL listed purge system suitable for C1D2
- a UL listed panel with a UL listed purge system
- not a UL listed panel but all internal components are listed for use in a C1D2 area OR have no make/break contacts and are in a GP enclosure as per 501.105(B) (3)
why?