Michael15956

Senior Member
Location
NE Ohio
I'm preparing a bid for re-lamping of the old existing fixtures which are not dust tight in a wood saw mill. Is this considered a classified location and governed by Article 506? The existing fixtures are fastened in place by plug and cord in a 20Ft. ceiling.

TIA
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
506 is based on the European "zone" system and covers what Articles 502 and 503 cover as far as classified areas go. The saw mill would most likely be a 503 application and not a 502 application. 503.130 does not require dust tight fixtures.
 