I have a Class 2 Div 2 Group F area classification that also needs to be resistant to ingress of water via hosedown. A nema 9 meets my hazardous location requirement but it is an indoor enclosure. I cannot find an enclosure that meets both requirements. Any suggestions
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I have a Class 2 Div 2 Group F area classification that also needs to be resistant to ingress of water via hosedown. A nema 9 meets my hazardous location requirement but it is an indoor enclosure. I cannot find an enclosure that meets both requirements. Any suggestions
There are enclosures that have both a NEMA 4 and a NEMA 9 rating. Take a look at this one Not sure exactly what type of enclosure you need. By the way, NEMA 9 is not suitable for Class II installations unless it is also marked NEMA 7.
 