Is there anything in the 2011 NEC that requires all ungrounded conductors to be opened by the light switch? I've seen 410.104(B) cited in similar situations but I can't see how a wall switch can be considered a 'switching device of auxiliary equipment.'

Each lighting circuit will be served by a 2-pole, lockable off, branch circuit breaker. The fixtures are 6-lamp T5HO and will be installed in a Class I, Div. 2 hazardous area.

Thanks.
 

iwire

Moderator
Staff member
Location
Massachusetts
The ballast is auxiliary equipment to the lamps.


410.104 Electric-Discharge Lamp Auxiliary Equipment.
(A) Enclosures.
Auxiliary equipment for electric-discharge
lamps shall be enclosed in noncombustible cases and treated
as sources of heat.

(B) Switching. Where supplied by the ungrounded conductors
of a circuit, the switching device of auxiliary equipment
shall simultaneously disconnect all conductors.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Unfortunately, the end result is that you will need to find full double-pole double-throw switches for the 3-way locations and four-pole double-throw (or four-pole crossover) switches for the 4-way locations.