    Ceiling fan issue

    Afternoon Gents,

    I'm a second year on the Commercial side and haven't done much Residential. Yesterday I decided that I wanted to run a receptacle into my bedroom. I crawled into the attic and found the junction box. I ran romex from the junction box into the stud bay that I wanted it in. I wire up the receptacle and now my ceiling fans that are in my living room won't turn off. So i bypassed the switch. I gave my Journeyman a call and he told me to put it back the way it was and send him a picture as well as do a wire diagram. After putting it back the way it was originally, my ceiling fans still won't turn off. I know this is something simple but I seem to be having a brain fart. Common among apprentices but to say the least i'm over here having a small pity party for myself haha. Any advice is welcome and appreciated, insults are extremely welcome lol.

    #2
    Chances are that the original junction box contained a switch leg ) two wire run to the wall switch. When done with 2 wire NM this puts one side of the switch on the white wire, and it would connect to the black wire going to the fan(s).
    If you reconnected the fan black wire to where the rest of the black wires were connected you would have bypassed the switch.
    My money is on that or a similar error if you did not individually mark your black wires before undoing the wire nut.

    Sent from my XT1585 using Tapatalk

    Comment


      #3
      Well, your lucky you have it the way you do. Generally a newbie wonders why the switch throws sparks and fire when he flips it the first time. Figure out which one goes to the switch and draw us a picture. Most likely you will answer own questions by the time you get that done.
      Tom
      TBLO

      Comment


        #4
        Also lucky, if it was a switch loop, that he didn't tie the white in with the neutrals. That's depending on where he tied in and where the switch loop started.
        [COLOR=navy]If you aim at nothing, you will hit it every time![/COLOR]

        Comment


          #5
          Originally posted by Little Bill View Post
          Also lucky, if it was a switch loop, that he didn't tie the white in with the neutrals. That's depending on where he tied in and where the switch loop started.
          Or if switch is also a speed controller, he maybe just fried it but it didn't draw enough to trip the breaker in the process.
          I live for today, I'm just a day behind.

          Comment


            #6
            180827-0704 EDT

            To unscramble the present mess consider the following assumong all wires are Romex:

            1. Separate all wires.

            2. With breaker on find the cable (2 wires and an EGC) with 120 V between hot and neutral. Verify that black to EGC is 120. This is your power source cable from the breaker. Label as power source.

            3. Verify that no other wires have voltage present relative to the source cable EGC.

            4. Turn the breaker off. Verify that none of the wires have voltage present relative to the source EGC wire.

            5. Assuming there is no open switch within the fan, then there will be continuity thru the fan of a number of ohms. Find this wire pair, and label as fan.

            6. Remaining should be one wire pair that goes to the wall switch. Using the continuity checker determine that this wire pair shows continuity or no continuity when the switch state is changed. If an ordinary toggle switch, then resistance should change from less than 1 ohm to infinity.

            Once the wires have been identified and that color coding is correct, then correctly connect the wires. And try the circuit.

            .

            Comment


              #7
              Gar, you should teach this.. and it works for wires coming through conduit, if you identify the conduits... only problem is if switch wire comes in as well on the homerun conduit but I have done it before...lol... Jamaican wiring problems...
              Student of electrical codes. Please Take others advice first.

              Comment


                #8
                180827-2123 EDT

                [COLOR=#000000]Adamjamma:

                [/COLOR]My method works even if all the wires are individual wires contained in one conduit, and some deduction. It just takes longer, and finding the correct ground or neutral reference wire to use.

                .

                Comment


                  #9
                  That’s what I mean.. you should teach it... I mean, my boss taught it to me in eighties just that way... but in conduit... yet I see so many who cannot figure it out... need fancy tracers to trace wires..lol...
                  Student of electrical codes. Please Take others advice first.

                  Comment


                    #10
                    Originally posted by gar View Post
                    180827-0704 EDT

                    To unscramble the present mess consider the following assumong all wires are Romex:

                    1. Separate all wires.

                    2. With breaker on find the cable (2 wires and an EGC) with 120 V between hot and neutral. Verify that black to EGC is 120. This is your power source cable from the breaker. Label as power source.

                    3. Verify that no other wires have voltage present relative to the source cable EGC.

                    4. Turn the breaker off. Verify that none of the wires have voltage present relative to the source EGC wire.

                    5. Assuming there is no open switch within the fan, then there will be continuity thru the fan of a number of ohms. Find this wire pair, and label as fan.

                    6. Remaining should be one wire pair that goes to the wall switch. Using the continuity checker determine that this wire pair shows continuity or no continuity when the switch state is changed. If an ordinary toggle switch, then resistance should change from less than 1 ohm to infinity.

                    Once the wires have been identified and that color coding is correct, then correctly connect the wires. And try the circuit.

                    .
                    Fixed it! I had my dad turn the switch on and off and went through the wires with my multimeter and measured ohms. ID'd the switch leg and the rest of the wires. Finding what the homerun was interesting. It's a knob and tube homerun. Used my voltage detector to find the neutral

                    Comment


                      #11
                      Originally posted by rob0311 View Post
                      Fixed it! I had my dad turn the switch on and off and went through the wires with my multimeter and measured ohms. ID'd the switch leg and the rest of the wires. Finding what the homerun was interesting. It's a knob and tube homerun. Used my voltage detector to find the neutral
                      Good job, have a cookie.

                      Ps. We do not insult apprentices trying to learn, we encourage them.
                      When you get your card, then we start insulting you!
                      [COLOR="blue"]"Electricity is really just organized lightning." George Carlin


                      Derek[/COLOR]

                      Comment


                        #12
                        Originally posted by jumper View Post
                        Good job, have a cookie.

                        Ps. We do not insult apprentices trying to learn, we encourage them.
                        When you get your card, then we start insulting you!
                        Roughly two more years until I can be properly insulted. Haha. I've already passed the test. Just need to bank hours.

                        Comment


                          #13
                          Originally posted by rob0311 View Post
                          Roughly two more years until I can be properly insulted. Haha. I've already passed the test. Just need to bank hours.
                          Hmmm...since you passed your test I wonder if there is an exception that allows us to start early.

                          CA lets people jw test before completing OJT hours? Interesting.
                          [COLOR="blue"]"Electricity is really just organized lightning." George Carlin


                          Derek[/COLOR]

                          Comment


                            #14
                            Originally posted by rob0311 View Post
                            Fixed it! I had my dad turn the switch on and off and went through the wires with my multimeter and measured ohms. ID'd the switch leg and the rest of the wires. Finding what the homerun was interesting. It's a knob and tube homerun. Used my voltage detector to find the neutral
                            Isn't it cheating to have a helper. You're supposed to crawl in and out of the attic at least 10 times to figure it out lol

                            Comment


                              #15
                              Originally posted by MattS87 View Post
                              Isn't it cheating to have a helper. You're supposed to crawl in and out of the attic at least 10 times to figure it out lol
                              Hardcore old school style. Love it!
                              [COLOR="blue"]"Electricity is really just organized lightning." George Carlin


                              Derek[/COLOR]