    EATON GFCI SGF15-M

    I am installing an EATON SGF15-M gfci receptacle under the sink. I am trying to make it a split circuit but I can’t find the “break off” tab. Does this model receptacle not have a break off tab?

    #2
    I have never seen a GFCI receptacle with break-off tabs.
    Master Electrician
    Electrical Contractor
    Richmond, VA

    Comment


      #3
      I have never seen an Eaton Receptacle
      They say I shot a man named Gray and took his wife to Italy
      She inherited a million bucks and when she died it came to me
      I can't help it if I'm lucky

      Comment


        #4
        Originally posted by lpfam111 View Post
        I am installing an EATON SGF15-M gfci receptacle under the sink. I am trying to make it a split circuit but I can’t find the “break off” tab. Does this model receptacle not have a break off tab?
        Remember there is a line and load so there is no way to get 2 circuits from one Gfci. Install a 2 gang box and use 2 gfci's
        They say I shot a man named Gray and took his wife to Italy
        She inherited a million bucks and when she died it came to me
        I can't help it if I'm lucky

        Comment


          #5
          Originally posted by lpfam111 View Post
          I am installing an EATON SGF15-M gfci receptacle under the sink. I am trying to make it a split circuit but I can’t find the “break off” tab. Does this model receptacle not have a break off tab?
          Push button resets are not allowed under sinks with cabinet doors, or behind cabinet doors at all.

          See "Readily Accessible" in new work code 210.8, and Replacement Code 406.4(D)
          Roger Ramjet NoFixNoPay

          Comment


            #6
            Originally posted by ramsy View Post
            Push button resets are not allowed under sinks with cabinet doors, or behind cabinet doors at all.

            See "Readily Accessible" in new work code 210.8, and Replacement Code 406.4(D)
            Yes they need to be readily accessible but it definitely arguable whether under a sink is readily accessible. IMO, if the receptacle is close to the front of the cabinet then it is considered readily accessible.

            I don't see anything that states it cannot be behind a door.
            They say I shot a man named Gray and took his wife to Italy
            She inherited a million bucks and when she died it came to me
            I can't help it if I'm lucky

            Comment


              #7
              Originally posted by Dennis Alwon View Post
              Remember there is a line and load so there is no way to get 2 circuits from one Gfci. Install a 2 gang box and use 2 gfci's
              There is a 2 gang box with 2 romex feeds. One is black red white gnd. That’s the one wired to the switch. The other romex is just black whit gnd but when I wire that to a second gfci it trips the breaker. The black red white works fine and operates by the switch.

              Comment


                #8
                Originally posted by Dennis Alwon View Post
                Yes they need to be readily accessible but it definitely arguable whether under a sink is readily accessible. IMO, if the receptacle is close to the front of the cabinet then it is considered readily accessible.

                I don't see anything that states it cannot be behind a door.
                I like your interpretation, but the senior planner who instructs our local IAEI tells inspectors to red tag it, forcing the reset placement elsewhere.

                I believe he uses this to force kitchen remodels to upgrade the electrical service when older panels won't except a GFCI breaker.
                Roger Ramjet NoFixNoPay

                Comment


                  #9
                  Originally posted by lpfam111 View Post
                  There is a 2 gang box with 2 romex feeds. One is black red white gnd. That’s the one wired to the switch. The other romex is just black whit gnd but when I wire that to a second gfci it trips the breaker. The black red white works fine and operates by the switch.

                  You do realize that we are not allowed to help with diy projects. I know you are an ee but unless you are qualified as an electrician then we cannot help.
                  They say I shot a man named Gray and took his wife to Italy
                  She inherited a million bucks and when she died it came to me
                  I can't help it if I'm lucky

                  Comment


                    #10
                    Originally posted by Dennis Alwon View Post
                    I have never seen an Eaton Receptacle
                    Eaton acquired Cooper.
                    I live for today, I'm just a day behind.

                    Comment