First post! Hope this makes sense!

So here is what we got going on. Owner of the shop we are wiring/remodeling want to turn 4 bays of lights on. From 2 different locations,3-way. Existing wiring has 3 switch legs in 4sq for 3 bays, feed by 2 circuits. Tied all lights together and they draw 17 amps. Is it possible to tie all lights together switched from 2 locations on 2 separate circuits?

Thanks guys!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Wire the coil as a load to a pair of 3-ways as you would for any light.

For your two circuits, use a 2-pole contactor. Wire each hot wire to a line terminal and each lighting group to the corresponding load terminal, as if each contact pair was a single-pole switch.

Neutrals wired together as usual.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190611-0814 EDT

I would use GE RR relays, and low voltage control. Now you can do all sorts of things. But most electricians seem to get totally confused by such systems.

.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
190611-0814 EDT

I would use GE RR relays, and low voltage control. Now you can do all sorts of things. But most electricians seem to get totally confused by such systems.

.
Those are indeed cool systems we service a number of retail places that originally had them, but a bit of a headache to get a simple time clock or occupancy sensor hooked in to one of those pulse controlled relays. I do like that they are actual latching contactors which are the next best thing to solid state.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190613-1430 EDT

tortuga:

I favor the RR over a solid-state for a couple reasons.

One, voltage drop in the millivolts compared to more than a 1 volt. That is a big difference in switch power dissipation.

Two, the RR is much less likely to fail under high transient voltage conditions than a solid-state unit.

Three, high ambient air temperature is less of a problem for the RR, than a solid-state.

If a time clock has separate NC and NO contacts, or a DPDT, but not a single SPDT output, then it is simple to pulse drive an RR. Requires a simple DC supply (a diode and transformer) to two RC filters with the filter capacitors separately connected to the NO and NC contacts. Each capacitor is made large enough to guarantee triggering of the RR (by memory possibly 500 to 1000 mfd), and the resistor made large to minimize power waste, but small enough to overcome capacitor leakage (possibly 10,000 to 100,000 ohms), and to recharge the capacitor in a reasonable time.

.
 