It seems that many (most?) Dimmers only put out about 90% of line side voltage :rant: Does anyone else know about this?
Well, there may be a diode droo or two, and a two terminal phase controlled dimmer has a hard task trying to maintain 100% conduction. It may be a consequence of inexpensive circuitry. Are you measuring with a true RMS meter? An averaging meter will give undue weight to the cutoff sections near the zero crossing.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190813-1333 EDT

A scope clearly shows the effect.

A phase shift dimmer essentially detects the time of a zero crossing, and initiates a time delay to triggering of the switch. This minimum time delay becomes a practical problem.

Probably the shortest possible time delay is set by a constant continuous current to the gate, and then the delay is a result of the characteristics of the switch. About a 1 volt switch voltage drop. At 1 V and a 120 V sine wave this is about arc sine of 1/170 = 0.24 degrees.

.
 
Meter is a klein branded true RMS meter so not the highest quality of course, but should be accurate. Dimmer is a lutron Caseta. Client said he heard about this and I was skeptical at first but a believer after I metered it with and without the dimmer.. they do have a high trim adjustment, but he said he had it set to max. I should have verified this but I didn't.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190814-2341 EDT

electrofellon:

I expect that you will find that virtually all commercial phase shift dimmers will show less than full voltage when set for maximum brightness.

.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
190814-2341 EDT

electrofellon:

I expect that you will find that virtually all commercial phase shift dimmers will show less than full voltage when set for maximum brightness.

.

And not as part of some energy saving conspiracy, but as a necessary consequence of economical design.
 
And not as part of some energy saving conspiracy, but as a necessary consequence of economical design.

I know Obama, the other libs, and big solar are behind this! So you really think it is just a coincidence that as soon as I bring this up, the forum get "upgraded" so everyone is all confused and disheveled so not as many people read this post!?!? Just kidding ;) But seriously, it is interesting that few people seem to know about this.
 
Last edited:

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
Any p-n junction will cause a voltage drop of ~0.7volts. Who knows how many junctions the power in a dimmer has to pass through to get to the other side!
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
You didn’t know this?
I thought it was more like 95% but it was enough that it could be slightly noticed in light output between hooking direct or installing dimmer.
I've known this since I was knee high to a grass-hopper, just the effects of being controlled by electronics.
But on the up-side, lamp life was extended just by installing a dimmer even if it was kept on high. Probably why many of the 65watt R30 lamps used in my can lighting are still in use today.
 

kwired

Electron manager
Location
NE Nebraska
I know Obama, the other libs, and big solar are behind this! So you really think it is just a coincidence that as soon as I bring this up, the forum get "upgraded" so everyone is all confused and disheveled so not as many people read this post!?!? Just kidding ;) But seriously, it is interesting that few people seem to know about this.

I could see that some may think it is possible that the solid state portions get bypassed when in full brightness position.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I could see that some may think it is possible that the solid state portions get bypassed when in full brightness position.

By adding a hardware switch at the max on position that could be done. Or by using a relay. But the users will see a jump from max variable to bypass/full. And it will be more expensive and harder to fit into a single gang format.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
There used to be a dimmer that looked like a standard toggle switch, but the toggle was actually the dimmer control. It had both mechanical-switch off and mechanical-switch fully-on bypass.

If 100% voltage is a requirement at times, parallel the dimmer with a switch.
 