Hey Fellas, I've got two metal halide fixtures on the front porch of two attached businesses, each one fed from a switch in that business. The complaint was that sometimes the fixtures turn off automaticly. I did notice that if you turn the switch off and back on the fixture goes off but never back on unless it is left off for a while. Ok is this normal and is this problem caused by voltage spikes and/or drops?
 

Nium

Senior Member
Location
Bethlehem, PA
Lamp or ballast is failing. Probably lamp. If a new lamp has recently been fitted then probably ballast.

It is normal for it to take up to 15 minutes for the lamps to come back on after having reached operating temperature and being switched off.
 

Rewire

Senior Member
If both fixtures are going off I would suspect a voltage fluxuation .If the fixture is going on and off fairly regularly then a bad capacitor may be the cause.It does take time for these fixtures to re light unless you install a restrike.
 

Rewire

Senior Member
Our supply house has a bulb tester .If you change the ballast kit put a new bulb in and use a sharpie to write the replacement date for future reference
 