NM Cable Temperature limitations

Status
Not open for further replies.

patron

Member
I have come across NEMA Bulletin No. 92 which states that when installing a recess light fixture with a required supply conductor insulation rating of 90 deg. in a house that is wired with type NM cable ( 60 deg.) you should install a junction box 18" away from the fixture and switch over to type NM-B cable ( 90 deg.) to run into the fixture. Is this a common practice? Does anyone really do this?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome to the Forum.
Seems a mute point to me as the only NM on the market for a number of years now has been NM-B.
If you happened to have a retrofit where some old (original) NM was is in use some transition would be necessary.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In this area, on retro-fit jobs whatever is installed must meet present Code, so some transition would be needed if the fixture called for 90? wiring.
 

patron

Member
Thanks to all who replied. I know this is a no brain er, but in all the classes and training that I have had over 20 years nobody ever pointed this out. I should have, but I never realized that the old NM was only rated at 60 deg. You never stop learning.
 