FIre Alarm Notificaiton Requirements in Residential High Rise Buildings

Status
Not open for further replies.

sirnightw

New member
Location
NY
Hi, I'm designing a High rise building in New Haven, CT. With 12 Floors of residential and 2 floors of mechanical... I understand the basics of the NFPA 72 and IRC to have smoke detectors in dwelling areas and notification devices in dwelling areas as well.

What I don't understand is if the public corridors, residential amenity spaces, or office spaces require Visual/Audible notification devices. My gut tells me to add notification devices to these areas where people will be working or walking around in the public areas, but I can't find in either of those codes where it requires those types of spaces to have that coverage.

I'd appreciate any input you can give.
 

dkidd

Senior Member
Location
here
Occupation
PE
IBC 2009

907.2.13 High-rise buildings. High-rise buildings shall be provided with an automatic smoke detection system in accordance with Section 907.2.13.1, a fire department communication system in accordance with Section 907.2.13.2 and an emergency voice/alarm communication system in accordance with Section 907.5.2.2. [F]
 