I have some under bench led lighting. 3"x8" flush mounted every 8 feet for about 200 feet in a concrete wall. 277V and I can use just one 20A circuit for them all.how often do I need a j box...do I even need them since I am daisy chaining the fixtures in the concrete wall and there are no splices?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
What wiring method you using? (PVC) Are the luminairs marked with a max size and number of conductors?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Not to be too picky, but how is 277v and 20 amps showing up in the "Low Voltage and Limited Energy" forum?
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I have some under bench led lighting. 3"x8" flush mounted every 8 feet for about 200 feet in a concrete wall. 277V and I can use just one 20A circuit for them all.how often do I need a j box...do I even need them since I am daisy chaining the fixtures in the concrete wall and there are no splices?
I would think you would only need the j-boxes at each light fixture, unless something unusual about your set up.
 