    class 2 wiring controling high voltage 4160

    question
    can control wiring (30V and under) for a piece of switch gear be installed in liquidtight flex through high voltage compartment to control box in high voltage compartment in the presence of high voltage wiring ?

    regards.

    #2
    Look at 300.3(C)(2)
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky

    Comment


      #3
      Originally posted by Dennis Alwon View Post
      Look at 300.3(C)(2)
      (2) Over 600 Volts, Nominal. Conductors of circuits rated over 600 volts, nominal, shall not occupy the same equipment wiring enclosure, cable, or raceway with conductors of circuits rated 600 volts, nominal, or less unless otherwise permitted in (C)(2)(a) through (C)(2)(e).

      Would this not be the application


      (d) In motors, switchgear and control assemblies, and similar equipment, conductors of different voltage ratings shall be permitted

      Comment


        #4
        See IN 1 for 300.3(C)(1)