Proper Installation of FA elevator control wiring in a hoistway.

Status
Not open for further replies.

Jtomson

New User
Location
Chipley,Fl
If FA control relays are permmitted to be installed in the elevator hoistway in a gutter..... Can they be installed in the same raceway as elevator power and control? As long as they are in their own conduit? What does the code specify what is and isnt allowed?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
If FA control relays are permmitted to be installed in the elevator hoistway in a gutter..... Can they be installed in the same raceway as elevator power and control? As long as they are in their own conduit? What does the code specify what is and isnt allowed?

As long as they are separated, I don't see a problem. At the FA relay, how are you keeping the LV and non-LV separated? Junction box with a divider?

Out of curiosity, is this one of those elevator controllers mounted in the hoistway or on top of the cab?
 