Harmonics interpretation electric board

Status
Not open for further replies.

KundaliniZero

Member
Location
CL
Hi, I saw some harmonics in a electric board so I would like to know what do you think.

It my first time seeing this value 30% THD is a lot for me, but I have no enough experience to know if this is usual.

Theory is different than experience.
dac43b637256eee2e9ce9241a9120803.jpg


Enviado desde mi TA-1039 mediante Tapatalk
 

ron

Senior Member
What is the load as a percentage of the meter full scale? At load relative load, high THD is not a big deal.

For example, if it was a 2000A meter and the load was 20A, a 30% THD is no big deal.

If the load is relatively high, what is the load type and what harmonic makes up the biggest offender? lots of triplen harmonic?
 

Besoeker

Senior Member
Location
UK
Hi, I saw some harmonics in a electric board so I would like to know what do you think.

It my first time seeing this value 30% THD is a lot for me, but I have no enough experience to know if this is usual.
Assuming the loads are single phase to neutral, 30% wouldn't altogether surprise me. Can you check the neutral?
 