    What do they mean by direct exhaust? As opposed to what?
    Attached Files

    #2
    Originally posted by mstrlucky74 View Post
    What do they mean by direct exhaust? As opposed to what?
    The code this is pulled from talks about supply air over 2,000 cfm. I would imagine direct exhaust would be exhaust fans that do not have any smoke/fire dampers in their ducts.

    In my experience, the only time we shutdown exhaust fans, other than smoke control, is if they feed through smoke/fire dampers. Stop the fan to avoid damage to the duct while the damper is closed.

    Comment


      #3
      Originally posted by ryant35 View Post
      The code this is pulled from talks about supply air over 2,000 cfm. I would imagine direct exhaust would be exhaust fans that do not have any smoke/fire dampers in their ducts.

      In my experience, the only time we shutdown exhaust fans, other than smoke control, is if they feed through smoke/fire dampers. Stop the fan to avoid damage to the duct while the damper is closed.
      This is not coming from a standard or code, but appears to be part of a specification or drawing note. A typical case where you might not want to shutdown an exhaust fan would be a Class 1 kitchen exhaust hood.

      Comment


        #4
        Thanks guys

        Sent from my SM-G955U using Tapatalk

        Comment


          #5
          IMHO direct exhaust fans exhaust directly to the outside either through ceiling or wall or possibly(?) through individual ducts that do not come together in a common plenum at any point.
          The distinction is that even if such fans pull in smoke or flame they do not aid in the spread of same to other parts of the building. Therefore they do not need to be shut down even if they are intaking smoke and therefore they do not need smoke detectors for a stop mechanism nor automatic stopping on alarm.