NAC & IDC ckts

Status
Not open for further replies.

ryant35

Member
Location
Cypress, CA
There isn't anything in the code that says they have to be separate. Your limitation will be per manufacturer, some required shielded wire if they are run together, due to noise as mentioned above.
Check with the wire requirements for the specific FACP you will be using.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
There isn't anything in the code that says they have to be separate. Your limitation will be per manufacturer, some required shielded wire if they are run together, due to noise as mentioned above.
Check with the wire requirements for the specific FACP you will be using.

^^^^What he said.
 