    NAC & IDC ckts

    Can they be in the same conduit per code? Thanks

    #2
    To generate more responses you need to specify what NAC and IDC mean.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

    Comment


      #3
      Originally posted by mstrlucky74 View Post
      Can they be in the same conduit per code? Thanks
      They can. Some IDC ckts are noisy and can induce sound on the nac. Clicking and very low chirping. Most common nuisance noise would be on a speaker ckt though so not too much concern if just horn/strobes.

      1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.

      Comment


        #4
        Originally posted by infinity View Post
        To generate more responses you need to specify what NAC and IDC mean.
        (NAC)Notification devices e.g. strobes, speaker/strobes- (IDC)Initiating devices e.g. pull stations, smokes etc.

        Comment


          #5
          There isn't anything in the code that says they have to be separate. Your limitation will be per manufacturer, some required shielded wire if they are run together, due to noise as mentioned above.
          Check with the wire requirements for the specific FACP you will be using.

          Comment


            #6
            Originally posted by ryant35 View Post
            There isn't anything in the code that says they have to be separate. Your limitation will be per manufacturer, some required shielded wire if they are run together, due to noise as mentioned above.
            Check with the wire requirements for the specific FACP you will be using.
            ^^^^What he said.

            Comment


              #7
              Originally posted by mstrlucky74 View Post
              Can they be in the same conduit per code? Thanks

              Yes, the code doesn't require them to be separate and can be run together. Your annunciator and LOC might be a different story.