2 HR FA AREAS

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Why the heck would they call for ALL wiring to be 2 hour rated even in sprinkler protected areas?
 

Attachments

  • Capture.jpg
    Capture.jpg
    25.1 KB · Views: 0

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Why the heck would they call for ALL wiring to be 2 hour rated even in sprinkler protected areas?

Purely opinion , but I think the intent of this note is to require 15 feet of separation between conductors and calling that separation (2 hours) probably comes from some guide book. Normally 5 feet is an acceptable separation or horizontal runs.
 

JFletcher

Senior Member
Location
Williamsburg, VA
would locating standard cable behind a 2 plus hour rated wall be acceptable? Aside from Mi cable, I am not aware of any wire or method that would still function in a fire
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
would locating standard cable behind a 2 plus hour rated wall be acceptable? Aside from Mi cable, I am not aware of any wire or method that would still function in a fire

VITALink® CIC would do it, but it doesn't meet some of the other requirements for NYC.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
What dies the 15' separation have to do with a 2 hour rating?

For certain occupancies, where the fire response is NOT immediate and total evacuation (airport, high rise), the notification devices must remain operable for 2 hours, along with anything else that facilitates their operation (Pathway Survivability Level 2). Normally you'd use VITALink or a similar product. In NYC, none of those products meet some of the other requirements of Local Law 39, so the city has crafted this alternative: Install the circuits as Class A AND separate not by 4 feet but by 15 feet, and we'll consider it the equal of Pathway Survivability Level 2. The exception is NOT supposed to use 15 foot separation and a 2-hour rated cable.
 

mstrlucky74

Senior Member
Location
NJ
For certain occupancies, where the fire response is NOT immediate and total evacuation (airport, high rise), the notification devices must remain operable for 2 hours, along with anything else that facilitates their operation (Pathway Survivability Level 2). Normally you'd use VITALink or a similar product. In NYC, none of those products meet some of the other requirements of Local Law 39, so the city has crafted this alternative: Install the circuits as Class A AND separate not by 4 feet but by 15 feet, and we'll consider it the equal of Pathway Survivability Level 2. The exception is NOT supposed to use 15 foot separation and a 2-hour rated cable.


So it's one or the other?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
No, it is the one, 15 feet of separation.

Plus Class A.

If you could find cable complying with LL 39 and being 2-hr fire resistive you could use it without Class A as NYC does not require everything to be Class A. The Port Authority, NJ Transit, LIRR, MTA, etc usually have internal standards that do require Class A, but the NYC code does not.
 