    Fire rated door contact

    Hello all,

    I have a fire inspector that is fighting me on our door contacts. They are installed in a fire rated steel door, I have been asked to provide a UL listing showing that it is fire rated, or replace it with one that is. I have had no luck confirming the fire rating (I don't believe it is). Below is a link to the UL listing for the current contact.

    http://database.ul.com/cgi-bin/XYV/t...183&sequence=1

    My question is, can anyone recommend a fire rated contact?

    Thanks in advance for your help.

    #2
    Not sure what kind you have by check this out

    https://stevenengineering.com/tech_s...C-CONTACTS.pdf

    go to model 1090

    BTW, welcome to the forum
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky

    Comment


      #3
      Thank you, I am not sure this will work for my application, but will help me in the future for sure.

      Any chance anyone was able to find a press fit version?

      And thank you

      Originally posted by Dennis Alwon View Post
      Not sure what kind you have by check this out

      https://stevenengineering.com/tech_s...C-CONTACTS.pdf

      go to model 1090

      BTW, welcome to the forum

      Comment


        #4
        Unless your switch is connected to the fire alarm or a fire alarm device, I'd say your inspector is over-reaching. If not and it needs to be listed, the manufacturer would say so and, more than likely, provide a sample manufacturer and part number.

        I think my concern would be with "modifying" a listed assembly by installing a press-fit contact. I've seen contractors have to "eat" labeled doors because they "modified" them. Rare, but it happens.

        Comment


          #5
          Originally posted by Rockyb View Post
          Hello all,

          I have a fire inspector that is fighting me on our door contacts. They are installed in a fire rated steel door, I have been asked to provide a UL listing showing that it is fire rated, or replace it with one that is. I have had no luck confirming the fire rating (I don't believe it is). Below is a link to the UL listing for the current contact.

          http://database.ul.com/cgi-bin/XYV/t...183&sequence=1

          My question is, can anyone recommend a fire rated contact?

          Thanks in advance for your help.
          Is he asking for a fire rated doorknob too?

          Comment


            #6
            I agree with this, the problem is we regularly install both press fit contacts and request to exits on door frames for our access control system. In this case, they questioned the REX, and that led to the contact as well.

            We may be heading towards eating the door frame.


            Originally posted by GrayHair View Post
            Unless your switch is connected to the fire alarm or a fire alarm device, I'd say your inspector is over-reaching. If not and it needs to be listed, the manufacturer would say so and, more than likely, provide a sample manufacturer and part number.

            I think my concern would be with "modifying" a listed assembly by installing a press-fit contact. I've seen contractors have to "eat" labeled doors because they "modified" them. Rare, but it happens.

            Comment


              #7
              Have it welded.
              Contact the people and ask them. TANE ALARM PRODUCTS

              Comment


                #8
                What does the door frame manufacturer, the RTE motion manufacturer and the door contact manufacturer say about it?

                Comment


                  #9
                  Originally posted by Rockyb View Post
                  Hello all,

                  I have a fire inspector that is fighting me on our door contacts. They are installed in a fire rated steel door, I have been asked to provide a UL listing showing that it is fire rated, or replace it with one that is. I have had no luck confirming the fire rating (I don't believe it is). Below is a link to the UL listing for the current contact.

                  http://database.ul.com/cgi-bin/XYV/t...183&sequence=1

                  My question is, can anyone recommend a fire rated contact?

                  Thanks in advance for your help.
                  I thought it was the DOOR that was fire rated? If it has a JB for the security box, then the DOOR was fire rated based on that design. What does the contact have to do with it.?

                  Comment