    NYC Pre-Action System

    Anyone know if they have to be in RGS conduit by NYC code?

    #2
    Ok, what's a Pre-Action system?

    -Hal

    Comment


      #3
      Originally posted by hbiss View Post
      Ok, what's a Pre-Action system?

      -Hal
      A type of sprinkler system that has supervisory air in the pipe and only allows water to flow into the pipe when the proper conditions activate, either detection (single interlock) OR detection & air exits the pipe (double interlock).

      NYC only allows single interlock.
      Ron

      Comment


        #4
        Originally posted by mstrlucky74 View Post
        Anyone know if they have to be in RGS conduit by NYC code?
        Yes, sort of but not exactly. You have a few other choices too. See NYC Electric Code Section 760.131(B) https://www1.nyc.gov/assets/building...rical_code.pdf
        Ron

        Comment


          #5
          Originally posted by ron View Post
          Yes, sort of but not exactly. You have a few other choices too. See NYC Electric Code Section 760.131(B) https://www1.nyc.gov/assets/building...rical_code.pdf
          Thanks

          Sent from my SM-N960U using Tapatalk

          Comment


            #6
            Originally posted by ron View Post
            A type of sprinkler system that has supervisory air in the pipe and only allows water to flow into the pipe when the proper conditions activate, either detection (single interlock) OR detection & air exits the pipe (double interlock).

            NYC only allows single interlock.
            Commonly called a dry system. There is an air compressor that keeps the piping charged with air.

            -Hal

            Comment


              #7
              Originally posted by hbiss View Post
              Commonly called a dry system. There is an air compressor that keeps the piping charged with air.

              -Hal
              Probably not worth arm wrestling about, but NFPA 13 defines them differently. Although pre-action systems normally have dry pipes in the protected area, it is different than a dry pipe system. A Pre-action system requires detection to activate.

              Technically there is such a thing as a non-interlock pre-action system that is essentially a dry pipe system, but nobody really goes through that listing process when a cheapo dry pipe system listing is easier and cheaper to get.
              Ron

              Comment