Announcement

Collapse
No announcement yet.

MMI install

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    MMI install

    Installing a remote MMI that controls a PLC via a Din plug class 2 cable, the remote MMI is being powered by a 24V DC 60 watt class 2 plug in wall transformer (wall wart) the box for the MMI is a steel hinged junction box. is it ok not to have a egc for the box?

    #2
    250(A) Alternating-Current Systems of Less Than 50 Volts.Alternating-current systems of less than 50 volts shall be grounded
    under any of the following conditions:
    (1) Where supplied by transformers, if the transformer
    supply system exceeds 150 volts to ground
    (2) Where supplied by transformers, if the transformer
    supply system is ungrounded
    (3) Where installed outside as overhead conductors.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

    Comment


      #3
      thats confusing, one thing though, my wall wart is 24VDC not AC, am I reading that correctly.

      Comment


        #4
        If all you have is Class 2 wiring and devices in that box, no, it doesn't have to be grounded- unless you think it may somehow become energized by some external source.

        -Hal

        Comment


          #5
          190503-2144 EDT

          wireday:

          What is "MMI"?

          From Wiki --- https://en.wikipedia.org/wiki/MMI

          So from that list Man Machine Interface seems the most logical.

          From your comment you said the power supply was 24 VDC output, but that is not your input.

          If your enclosure is metal I would ground it independent of any rules. You said metal box. So I would connect that box to adjacent metal objects. Note: an EGC can have up to or possibly more than the source voltage on it under short circuit conditions. Somewhere in the past I have indicated how this can happen.

          If whatever this device is totally insulated, and it is designed such that anything an operator could touch is non-conductive, then I would see no need for grounding.

          In general I would not assume any power supply from 120 to 24 V could not develop an internal short. I can design one that has an extremely low probability of a shorting failure, but I can not generally assume this for any commercial product.

          .

          Comment

          Working...
          X