    Hello all. I am creating an outage schedule for a construction project at a facility and was wondering if it is necessary to disconnect power to a new switchboard in order to install cables feeding several motor loads, or if this work can be done by simply opening the affected feeder breakers?

    Thank you for your time.
    +++Da Big Mek+++

    #2
    The short answer is the power needs to be shut down in accordance with OSHA and NFPA 70E, the long answer involves "hot work" permits, PPE, and a reason that the equipment can not be shut down.

    Roger
    Moderator

    Comment


      #3
      Thanks for the help!
      +++Da Big Mek+++