    Say a note that said all fire alarm conduits must have #10 ground wire. Anyone ever see this. Makes no sense.

    #2
    FA CONDUIT WIRE

    Yes for supplying power to control panels, etc.

    See NYC 2011 electrical code 760.33(B)

    Joe Villani

    Comment


      #3
      Makes no sense? It's a Code book. Sense only comes into half of the reasons for codes.

      Comment


        #4
        Originally posted by Joe Villani View Post
        Yes for supplying power to control panels, etc.

        See NYC 2011 electrical code 760.33(B)

        Joe Villani
        Hey Joe. Still don't get it. Power to FACP's, DGPS etc. is run separately from FCO's. I thought that note meant ALL fire alarm conduits meaning even those running to smokes, strobes etc.

        Comment


          #5
          Originally posted by mstrlucky74 View Post
          Hey Joe. Still don't get it. Power to FACP's, DGPS etc. is run separately from FCO's. I thought that note meant ALL fire alarm conduits meaning even those running to smokes, strobes etc.
          That sounds silly.
          Rob

          Moderator

          All responses based on the 2014 NEC unless otherwise noted

          Comment


            #6
            Agree..[emoji16]...just have to be sure when they say ALL fire alarm conduits..what would you think?

            Sent from my SM-N960U using Tapatalk

            Comment


              #7
              Originally posted by mstrlucky74 View Post
              Agree..[emoji16]...just have to be sure when they say ALL fire alarm conduits..what would you think?
              I don't think that it's required so an RFI is in order.
              Rob

              Moderator

              All responses based on the 2014 NEC unless otherwise noted

              Comment


                #8
                Who comes up with this stuff?