    Voltage Separation

    A concrete floor containing low and 120v wiring conduits have been damaged and are being replaced into an installed box. I thought there was a code req separation of voltages, not in ch3, not in ch1, or ch2. I know it's there. I think it's there?
    Any ideas?

    #2
    800.133.A.2 what you are looking for?

    Comment


      #3
      Originally posted by Chamuit View Post
      800.133.A.2 what you are looking for?
      Thanks for the chapter 8 stuff.
      No I thought there was req's about separation barriers installed in pannels, boxes. ect. Guess I must have imagined it.

      Thanks

      Comment


        #4
        Originally posted by Russell Ensslin View Post
        A concrete floor containing low and 120v wiring conduits have been damaged and are being replaced into an installed box. I thought there was a code req separation of voltages, not in ch3, not in ch1, or ch2. I know it's there. I think it's there?
        Any ideas?
        It is likely that these can not be in the same box. Is this a class 2 circuit?

        Comment


          #5
          Originally posted by texie View Post
          It is likely that these can not be in the same box. Is this a class 2 circuit?
          Yes
          What about a barrier?


          Sent from my iPhone using Tapatalk

          Comment


            #6
            Originally posted by Russell Ensslin View Post
            Yes
            What about a barrier?


            Sent from my iPhone using Tapatalk
            that would work. Barriers are available for 4 square boxes.

            Comment


              #7
              800.133.A.1 ex #1 & #2 then.

              Comment


                #8
                Hope the topic isn’t dead but I still need code for the separation of low (120)and high voltage208^ in the same box


                Sent from my iPhone using Tapatalk

                Comment


                  #9
                  Originally posted by Russell Ensslin View Post
                  Hope the topic isn’t dead but I still need code for the separation of low (120)and high voltage208^ in the same box

                  There is none, 120, 240, 277, 480, are allowed in the same raceways and enclosures, see 300.3(C). Higher and lower voltages have some particulars that needs to be adhered to.

                  There are also concerns if devices are in the same box with multiple voltages.



                  Roger
                  Moderator

                  Comment


                    #10
                    Originally posted by Russell Ensslin View Post
                    Hope the topic isn’t dead but I still need code for the separation of low (120)and high voltage208^ in the same box


                    Sent from my iPhone using Tapatalk
                    208 is 120 to ground.
                    Please see 300.3(C)(1)
                    And the IN at the end, most miss this, and try to use a class 2 circuit with 600 volt insulation in a raceway with power and lighting.
                    Moderator-Washington State
                    Ancora Imparo