    Fire Alarm power supply conductoors

    Is it OK to run a dedicated 120V branch circuit for a fire alarm in the same conduit with other non-fire alarm 120V branch circuits?

    #2
    Originally posted by jmanderson View Post
    Is it OK to run a dedicated 120V branch circuit for a fire alarm in the same conduit with other non-fire alarm 120V branch circuits?
    For the 120V only, yes.